Additional IFC-Bench v2 reference-answer corrections for eight MEP questions

#14
by GiocondoGiocoso - opened

While validating IFC-Bench v2 against the source IFC files, I found 13 reference-answer discrepancies. Could you review the corrections below? 5 of them were already mentioned at PR #13. and these are additional 5 errors

samuel_macalister_sample_house / mep.ifc

  • Q723: There are 153 rigid duct segments and 59 flexible segments.
    The reported rigid count of 207 includes 54 flexible segments. With
    155 fittings, 43 air terminals, and 4 dampers, the corrected total is 414.
  • Q724: The seven listed electrical component counts sum to 191.
    The reference reports 190.
  • Q729: The seven sensors are four movement sensors, two flow sensors,
    and one heat sensor. The reference describes all seven as temperature
    monitoring sensors.
  • Q730: Only MB01 is on the ground floor (00. Begane grond).
    Data board 1 and SB 02 are on 01. verdieping, according to IFC containment.
  • Q736: Both unitary equipment types are designated AIRHANDLER.
    In particular, AH-240913151652 is classified as HVAC equipment in the IFC,
    while the reference labels it plumbing equipment.

sixty5 / electrical.ifc

  • Q849: The 283 cable-connection candidates are a subset of the
    1,309 conduit fittings. Under the reference's counting scope, there
    are 5,733 distinct objects (4,424 + 1,309). The reported total of 6,016
    counts the subset twice. The corresponding densities are 301.74 per
    defined storey and 50.87 per 100 m of conduit.

wbdg_office / mep.ifc

  • Q1001: There are 126 supply and 119 return air terminals with flow
    data, for 245 terminals. Their stored flow values sum to 1,045.667
    for supply and 987.575 for return, or 2,033.242 combined. The mean is
    8.299 in each group. The IFC stores these values as IfcReal without
    an explicit property unit, so the counts and raw totals are directly
    reproducible and the unit attribution needs confirmation.
  • Q1010: The building has nine panelboards and two transformers,
    for 11 devices. The six panelboards reported in the reference are
    those on Level 1. The other three are on Level 2.