GENCO meets friends: Foundation Model Mixing for a Full Dynamic All-Electric Society

#26
by Obi71200 - opened

Marco Obermeier
Julius-Maximilians-Universität Würzburg, Germany
Weihenstephan-Triesdorf University of Applied Sciences, Freising, Germany

Working paper, data and code: Zenodo, DOI 10.5281/zenodo.23622826

1. Introduction

Distribution grids are planned for the worst case, so new connections can be refused although much of the capacity is free most of the time (existing grids contain untapped capacity that varies by location and time [1]). Dynamic tariffs and flexible connection agreements could shift batteries, heat pumps and vehicle charging into the free capacity and avoid reinforcement. To do so safely, grid operators have to plan ahead and know, for example one day ahead, how the shifted demand loads each line and transformer. This requires the available capacity of every line and transformer for the next day: the margin between expected flow and rating, in import and export (Figure 1).

The idea is to integrate the grid foundation model GENCO [2] into such a day-ahead workflow and to test how well it finds the available capacity compared with classical state estimation (Figure 2). Grid foundation models have so far been tested on transmission grids, mostly synthetic [2]–[5]. In real distribution grids the model is uncertain and only some elements are measured [6], [7]. Great Britain is one of the few countries whose distribution grid operators publish topology data and measurements openly (Section 2). The test therefore runs on a real British grid, Ninfield, where about half of the elements are measured.

The workflow needs three steps: a grid model from topology data, the flows on it from measurements, and their forecast for the next day. Each step can be taken by a different kind of foundation model, and this is what foundation model mixing means here: a large language model builds the grid model, a grid foundation model estimates the flows and a time series foundation model forecasts them. In this study, an AI agent on a large language model builds the grid model from topology data, as teams of grid operators do today, and the time series foundation model Timestral-209M [8], a zero-shot model evaluated on GIFT-Eval [9], forecasts the flows. Two paths estimate the flows on this grid model:

  • Classical path (operator workflow emulated by agentic AI): weighted least squares (WLS), the state estimation of grid operators, fits the power flow equations of the grid model to the measurements.
  • GENCO path: the grid foundation model GENCO, pretrained on power flow in other grids, takes the same grid model and measurements as a graph and is fine-tuned on this grid’s measurements.

This leads to three lead questions: how GENCO can be integrated into a real day-ahead workflow, from topology data and measurements to available capacity, whether it finds the available capacity with a lower error than classical state estimation, and what this capacity is worth for flexibility, for example batteries.

Figure 1: Available capacity. The margin between the day-ahead flow forecast and ±rating of one line (schematic). Colour shows the available capacity for additional demand, hatching the shifted demand, green the flow after the shift and the dotted line the worst-case peak.

Figure 2: Idea and workflow. How the classical path and the GENCO path determine and use the available capacity. The numbers match the steps in Section 3 and Figure 4.

2. Grid and data

Distribution grid data are rarely openly available, but Great Britain is an exception. Its operators publish a Long Term Development Statement (LTDS) [10] and treat their data as presumed open [11]. The grid and measurement data come from the UK Power Networks (UKPN) Open Data Portal [12] under CC BY 4.0. Weather, prices and exchange rates come from Open-Meteo, Elexon and the ECB. The main test grid is Ninfield (A) in the South East, the part of the grid fed from the 400 kV transmission grid at the Ninfield grid supply point (Figure 3). Two further grids, rural Burwell (B, 311 buses) and urban Norwich (C, 237 buses), test whether the results transfer to other grids.

2.1 Data

Grid model: The LTDS gives the buses, lines, cables and transformers with their winter ratings [13]–[16]. For Ninfield these are 263 buses at 132, 33 and 11/6.6 kV, 264 with the 400 kV grid supply point.

Measurements: UKPN publishes half-hourly operational measurements of the flows on its 132 kV circuits [17], transformers 132/33 kV [18], 33 kV circuits [19] and transformers to 11 and 6.6 kV [20]. They are used from January 2024 to September 2026 (44,107 usable half-hours). Mostly the current I is published, in Ninfield at 142 elements, active power P also at 23 of them and reactive power Q at none. Apparent power S follows from I and the nominal voltage. These measurements are both the input of the two paths and the reference against which their estimates are checked.

PV, wind, batteries, weather: The installed capacities come from the UKPN Embedded Capacity Register [21], [22], rooftop PV from UKPN’s Distribution Future Energy Scenarios (DFES) [23]. Actual and day-ahead weather from Open-Meteo [24] serves as additional input (covariates) of the Timestral-209M forecast.

Prices: Hourly spot market prices of Great Britain from Elexon [25], converted to EUR at the mean ECB rate [26]. Day-ahead prices are not openly available for Great Britain.

Scenario 2035: The DFES pathway with the highest 2035 growth of heat pumps, electric vehicles and rooftop PV in Ninfield (Electric Engagement) adds the 2035 demand of vehicles and heat pumps and the 2035 rooftop PV generation per bus to the measured 2026 net load. On the test days of 2026, it raises the highest daily loading of any element from 72 to 128 % of rating on average and lifts five elements above their rating without flexibility. Step ⑤ in Section 3 uses it for the battery schedule.

Burwell and Norwich come from the same sources and run through the same workflow.

2.2 Data preparation and quality

Only about half of the circuits and transformers in the grid models are measured, least at 33 kV (27 to 32 %). The flows on the others have to be estimated by each path. Where only the current is measured, P and Q follow from the current and the power factor given in the LTDS. All preparation steps and settings are in the Zenodo record.

measured / in the model (circuits and transformers) A Ninfield B Burwell C Norwich
132 kV circuits 15 / 22 (68 %) 19 / 25 (76 %) 22 / 24 (92 %)
transformers 132/33 kV 10 / 19 (53 %) 10 / 14 (71 %) 12 / 12 (100 %)
33 kV circuits 46 / 161 (29 %) 57 / 180 (32 %) 41 / 151 (27 %)
transformers to 11 and 6.6 kV 71 / 81 (88 %) 56 / 73 (77 %) 89 / 89 (100 %)
all 142 / 283 (50 %) 142 / 292 (49 %) 164 / 276 (59 %)

Table 1: Measurement coverage. Measured elements / elements in the grid model (share), per voltage level and grid.

Figure 3: Ninfield grid model. Voltage levels and sites, transformers marked as measured or not, and the number of 33 kV circuits per site.

3. Method

The method follows the five steps of Figure 2. These are ① build the grid model, ② forecast the next day, ③ estimate the current flows, ④ compute the next day’s flows and ⑤ plan batteries on them. Both paths use the same data and are checked against the same measurements. They differ only in how the flows are estimated.

① grid model: An AI agent [27] builds an AC grid model in pandapower [28] from the LTDS (264 buses). WLS runs on this model. GENCO runs on a reduced version of it: buses joined by closed couplers or very short lines are merged, so 264 buses become 211. Exact AC on both models differs by 0.003 % on 600 cases. The flows of merged measured circuits follow from the power balance at their buses, so all measured elements are evaluated on both.

  • classical path: WLS (weighted least squares), the standard state estimator of grid operators [29], with Huber weights (3 σ) and at most 25 iterations.
  • GENCO path: GENCO starts from gridfm/genco-pf-transfer [30], the power flow model used for unseen grids in the GENCO paper [2], and is fine-tuned on measurements up to June 2025 with the optimiser hyperparameters of the GENCO paper (batch 64, learning rate 5e-4 with decay, at most 80 epochs). The training loss is the WLS objective: the weighted squared difference between estimated and measured flows.

② forecast: Timestral-209M, zero-shot, issued at noon UTC the day before (2,048 hours of context, temperature and radiation as covariates), for the net load of every bus and every measured flow, against a naive forecast (latest known value of the same half-hour).

③ state estimation (now): tests how well a path estimates flows where nothing is measured. The measured elements of each type are split into five groups. Each group is hidden in turn, and its flows are estimated from the other measurements only, as if those meters did not exist. A hidden 33 kV circuit, for example, is estimated from its neighbours. Two variants are calibrated on the validation set, the second half of 2025 (Section 4): GENCO alone gets one bias correction per element type, and GENCO + WLS averages WLS-AC, WLS-DC and GENCO with one weight per element type.

④ day-ahead power flow (tomorrow): computes the next day’s flows from the forecast of ② for the net load at each bus. WLS-AC and WLS-DC run an AC and a DC power flow on the grid model of ①, GENCO takes the same forecast as input. Nothing is hidden, because on the day before no measurement of the next day exists. All measurements of the next day serve as reference.

⑤ battery schedule against the flow: tests what the available capacity is worth for flexibility. Batteries serve as the example, as a common flexibility whose schedule can be set freely within power and energy limits. A battery sits at each of the 63 load buses (47 at 11 and 6.6 kV, 11 at 33 kV, 5 at 132 kV), with 20 % of the bus’s 2025 peak, 2 hours of energy and a round-trip efficiency of 90 % (166 MW in total). Sizes up to 100 % of the bus peak (832 MW) test the dependence on size.

The battery model is a linear programme: it sets the power of each battery in each hour, keeps power and energy within their limits and ends the day at the starting state of charge. Linear sensitivities give how much one MW at a battery changes the flow on each element, for the switching state of that day. Each path runs the battery model once per day, with all limits from its own day-ahead power flow (tomorrow). Three operating modes differ only in their objective:

operating mode objective grid limit
(a) grid-serving lowest forecast daily peak loading no element above its rating
(b) market with grid limit highest revenue no element above its rating
(c) mixed highest revenue no element above the forecast peak of (a)

A market schedule without any grid limit is the reference for revenue. Prices are the spot market prices of Section 2.1, assumed known in advance. All paths except perfect foresight plan on the same Timestral-209M forecast of ② and differ only in the power flow (exact AC, DC, GENCO or their mix). Perfect foresight plans on the actual state, on which all schedules are evaluated, and so gives the upper bound within this linearised model.

The actual state is the flow of ① with the actual loads plus the change the batteries cause through the same linear sensitivities. Each schedule is evaluated on it on 249 of the 263 test days. The other days lack 24 valid hours or a known switching state. Three metrics:

  1. peak reduction: how much the schedule lowers the day’s highest actual loading over all elements, also as a share of the perfect-foresight reduction
  2. revenue: EUR per MW of battery power and year (249 days scaled to 365)
  3. hours above rating: hours in which the schedule pushes an element above its rating, summed over the elements, with the number of elements concerned

The same evaluation runs for the scenario 2035 (Section 2).

4. Evaluation setup

Periods: Training from January 2024 to June 2025, validation 2025 H2, test the 263 days from January to September 2026 with a complete forecast. All choices of every path (variants, weights, bias correction) are made on the validation set, the WLS settings by cross-validation on 2024 and 2025. The test set does not overlap with training or any choice, except one PV scaling factor per grid for B and C (Limits).

Tests: A2026 is the test on A in 2026, likewise B2026 and C2026. B and C check whether the workflow transfers without new choices. GENCO is fine-tuned on each grid’s own measurements, and only the bias correction of GENCO alone is refitted on each grid’s validation set. Step ⑤ also runs on the scenario 2035 (Section 2.1).

Metric: The rating sets the available capacity, so all errors are given in % of the element’s rating (3 % on a 100 MVA transformer means 3 MVA): the absolute error of the apparent power |S| per element and hour, averaged per element type and then with equal weight over transformers to 11/6.6 kV, 33 kV circuits and grid transformers. The measured loading averages 16.5 % of the rating, so the errors are also given relative to the measured flow (nMAE: sum of absolute errors divided by the sum of measured flows), as the GENCO paper relates its error to the mean injection [2].

Daily peak error: The highest forecast loading of any element per day minus the highest actual one, in % of rating and averaged over the test days, with the share of days on which the peak is underestimated. It is the quantity the grid-serving mode of ⑤ lowers.

5. Results

5.1 How well does each path find the available capacity?

In A2026, GENCO + WLS had a mean error of 3.52 % of rating in state estimation (now) and 3.20 % in the day-ahead power flow (tomorrow). WLS-AC had 3.83 and 3.43 %. In the mean of B2026 and C2026, GENCO + WLS had 5.00 and 4.78 %, against 4.29 and 3.41 % for WLS-AC. In the day-ahead power flow (tomorrow), WLS-AC underestimates the daily peak by 1.0 % of rating on 49 % of the days and GENCO + WLS by 16.7 % on 92 % of the days. Both overstate the available capacity at the peak.

Figure 4: Evaluation chain, A2026, steps as in Figure 2: ① grid model with actual loads, ② Timestral-209M against the naive forecast, ③ and ④ available capacity error per element and path, metrics as in Section 4.

5.2 What is the available capacity worth?

Grid-serving, the batteries of ⑤ achieved 61 % of the perfect-foresight reduction on the WLS-AC day-ahead power flow (tomorrow) and 44 % on GENCO + WLS. In mixed mode, perfect foresight keeps the full reduction at 96 % of the revenue of the market without grid limit, and no day-ahead path reaches the full reduction. In the scenario 2035, five elements lie above their rating already without batteries (1745 hours). Grid-serving, the day-ahead paths reach 91 to 94 % of the perfect-foresight reduction but add 90 to 274 hours above rating. An exact AC check of the schedules on 12 days confirms the linear sensitivities (correlation 0.997).

Figure 5: Battery schedule over the battery size, A2026 and scenario 2035, 90 % round-trip efficiency, battery sizes up to 100 % of the bus peak (832 MW), tables at 166 MW.

6. Discussion

6.1 How can GENCO be integrated into a real day-ahead workflow?

GENCO took the same grid model, measurements and forecast as WLS, but needed fine-tuning on the grid’s own measurements. The AI agent built the grid model from topology data, and Timestral-209M forecast the next day zero-shot. As a power flow on the actual loads of ①, GENCO had 7.39 % of rating zero-shot (could larger grid foundation models improve zero-shot so far that no fine-tuning is needed?) and 4.90 % fine-tuned, against 2.97 % for the exact AC power flow.

6.2 Does GENCO find the available capacity with a lower error?

Only on the grid it was tuned on: in the day-ahead power flow (tomorrow), GENCO + WLS had 3.20 % on Ninfield against 3.43 % for WLS-AC, but 4.78 % on the transferred grids against 3.41 %. With batteries, WLS-AC reached 61 % of the perfect-foresight reduction in 2026 and 93 % in 2035, GENCO + WLS 44 and 91 %. Most of the error does not come from the forecast: with the actual loads, the exact AC power flow of ① already had 2.97 % of rating, against 3.43 % for WLS-AC on the forecast. This remaining error lies in the grid model and the measurement data, which this study does not separate.

6.3 What is the available capacity worth for flexibility?

In 2026 the grid is mostly free, with a measured loading of 16.5 % of rating on average. On the same days, the scenario 2035 raises the highest daily loading of any element from 72 to 128 % of rating on average. With perfect foresight, the mixed mode keeps the full peak reduction at 96 % of the revenue of the market without grid limit. With the day-ahead paths, revenue stays at 95 to 98 %, but only 44 % (WLS-AC) and 27 % (GENCO + WLS) of the perfect-foresight reduction remain in 2026, and 87 and 82 % in 2035. The mixed mode fills the room below the forecast peak, so an underestimated peak rises, and GENCO + WLS underestimates it on 92 % of the days, WLS-AC on 49 %. For flexibility, the error at the daily peak decides, not the mean error. ⑤ evaluates all schedules on the grid model of ①, so there exact AC differs from perfect foresight only in the load forecast of ②. The forecast alone costs 39 % of the grid-serving reduction in 2026, and the error of the grid model and data comes on top in a real grid.

Limits

Data: Only half of the circuits and transformers are measured (Table 1), P at 23 of them in Ninfield and Q at none. The other half can neither train GENCO nor test any path. Q at the load buses follows from a power factor, ratings are LTDS winter values, and for B and C one PV scaling factor per grid was fitted on all years including the test.

Evaluation: All choices were made on one grid, with one test period and one training seed per GENCO model. With the low loading of 2026, errors in % of rating are small and the grid limit of mode (b) rarely binds. Only the scenario 2035 loads the grid near its rating.

Battery model: ⑤ uses linear sensitivities and active power only and evaluates on the grid model of ①, so the error of the grid model is not included. Revenue covers the spot market only, with prices known in advance and the nine test months scaled to a year.

7. Conclusion

The workflow runs end to end on a real grid and the free capacity is there, but the day-ahead estimates do not yet find the daily peak well enough to use it. An AI agent built the grid model, Timestral-209M forecast the next day zero-shot, and GENCO entered the workflow after fine-tuning with the WLS objective as loss, which needs measurements only, not known grid states. GENCO + WLS had the lower error only on the grid it was tuned on, and the classical path kept the larger share of the peak reduction with batteries, now and in 2035. The two limits are the forecast of the daily peak and the grid model and measurement data. The workflow is a first step towards a full dynamic all-electric society that uses the free grid capacity day by day, not a finished solution, and further work will test other approaches for these two limits.

Acknowledgements

I thank the GridFM community for the challenge and the published models, and the open science and open source communities whose data, models and software made this work possible.

Declaration

AI assistants helped to write and revise code and text. The author set the idea and the method and checked the main results. This is a working paper, and results may still change. Prepared for the GridFM Challenge with GENCO, GridFM Conference, Porto, Portugal, 29–30 October 2026.

Text and data: CC BY 4.0, code: Apache License 2.0. Contains UK Power Networks data (CC BY 4.0, modified), Open-Meteo.com weather data (CC BY 4.0), BMRS data © Elexon Limited copyright and database right 2026 and ECB statistics (own calculation). Third-party data and model weights are not redistributed.

References

Show all 30 references

[1] International Energy Agency, “Modernising grids in the age of electricity: Scaling digital technologies and AI for better use of existing networks,” IEA, Paris, 2026. Available: https://iea.blob.core.windows.net/assets/ebd98036-db76-4347-b498-4b18d73fe305/ModernisingGridsintheAgeofElectricity.pdf

[2] A. Puech et al., “GENCO – a unified neural solver embedded in a development framework for steady-state grid analysis.” arXiv:2608.09921, 2026. Available: https://arxiv.org/abs/2608.09921

[3] H. F. Hamann, B. Gjorgiev, T. Brunschwiler, L. S. A. Martins, et al., “Foundation models for the electric power grid,” Joule, vol. 8, no. 12, pp. 3245–3258, 2024, doi: 10.1016/j.joule.2024.11.002.

[4] Weijie1996, “Transformer tap position identification with GENCO under fuzzy measurements.” GENCO Challenge, entry #12, Hugging Face, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://huggingface.co/spaces/gridfm/genco-challenge/discussions/12

[5] oriolh, “Cloud2Grid: From clouds to grid to value.” GENCO Challenge, entry #14, Hugging Face, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://huggingface.co/spaces/gridfm/genco-challenge/discussions/14

[6] A. Primadianto and C.-N. Lu, “A review on distribution system state estimation,” IEEE Transactions on Power Systems, vol. 32, no. 5, pp. 3875–3883, 2017, doi: 10.1109/TPWRS.2016.2632156.

[7] K. Dehghanpour, Z. Wang, J. Wang, Y. Yuan, et al., “A survey on state estimation techniques and challenges in smart distribution systems,” IEEE Transactions on Smart Grid, vol. 10, no. 2, pp. 2312–2322, 2019, doi: 10.1109/TSG.2018.2870600.

[8] Mistral AI, “Timestral-209M (model weights).” Hugging Face, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://huggingface.co/mistralai/Timestral-209M

[9] T. Aksu et al., “GIFT-Eval: A benchmark for general time series forecasting model evaluation.” 2024. doi: 10.48550/arXiv.2410.10393.

[10] Ofgem, “Form of Long Term Development Statement, direction under Standard Licence Condition 25 of the electricity distribution licence.” 2024. Accessed: Oct. 24, 2026. [Online]. Available: https://www.ofgem.gov.uk/sites/default/files/2024-04/Form%20of%20Long%20Term%20Development%20Statement%20300424.pdf

[11] Ofgem, “Data Best Practice Guidance, version 2.0.” 2023. Accessed: Oct. 24, 2026. [Online]. Available: https://www.ofgem.gov.uk/sites/default/files/2023-08/Track%20Changes%20Data%20Best%20Practice%20Guidance%20v2.0.pdf

[12] UK Power Networks, “UK Power Networks open data portal.” 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/

[13] UK Power Networks, “LTDS table 1: Circuit data.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-ltds-table-1-circuit-data/

[14] UK Power Networks, “LTDS table 2a: Two-winding transformer data.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-ltds-table-2a-transformer-2w/

[15] UK Power Networks, “LTDS table 3a: Observed load data.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-ltds-table-3a-load-data-observed/

[16] UK Power Networks, “LTDS table 5: Generation data.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-ltds-table-5-generation/

[17] UK Power Networks, “132 kV circuit operational data, half-hourly.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-132kv-circuit-operational-data-half-hourly/

[18] UK Power Networks, “Grid transformer operational data, half-hourly.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-grid-transformer-operational-data-half-hourly/

[19] UK Power Networks, “33 kV circuit operational data, half-hourly, SPN.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-33kv-circuit-operational-data-half-hourly-spn/

[20] UK Power Networks, “Primary transformer power flow, historic half-hourly, SPN.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-primary-transformer-power-flow-historic-half-hourly-spn/

[21] UK Power Networks, “Embedded capacity register, 1 MW and above.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-embedded-capacity-register/

[22] UK Power Networks, “Embedded capacity register, under 1 MW.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-embedded-capacity-register-1-under-1mw/

[23] UK Power Networks, “Distribution future energy scenarios by local authority.” UKPN Open Data Portal, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://ukpowernetworks.opendatasoft.com/explore/dataset/ukpn-dfes-by-local-authorities/

[24] Open-Meteo, “Historical weather API and previous runs API.” 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://open-meteo.com/

[25] Elexon, “Market index data (MID), APX market index price.” Balancing Mechanism Reporting Service (BMRS), 2026. Accessed: Oct. 25, 2026. [Online]. Available: https://data.elexon.co.uk/bmrs/api/v1/datasets/MID

[26] European Central Bank, “Euro foreign exchange reference rates, GBP per EUR (EXR.D.GBP.EUR.SP00.A).” ECB Data Portal, 2026. Accessed: Oct. 25, 2026. [Online]. Available: https://data.ecb.europa.eu/data/datasets/EXR/EXR.D.GBP.EUR.SP00.A

[27] Anthropic, “Claude Code.” 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://claude.com/claude-code

[28] L. Thurner et al., “pandapower—an open-source Python tool for convenient modeling, analysis, and optimization of electric power systems,” IEEE Transactions on Power Systems, vol. 33, no. 6, pp. 6510–6521, 2018, doi: 10.1109/TPWRS.2018.2829021.

[29] A. Abur and A. Gómez Expósito, Power system state estimation: Theory and implementation. CRC Press, 2004. doi: 10.1201/9780203913673.

[30] gridfm, “genco-pf-transfer (model weights).” Hugging Face, 2026. Accessed: Oct. 20, 2026. [Online]. Available: https://huggingface.co/gridfm/genco-pf-transfer