GENCO in the Loop: Grid-to-Task Adaptation and Physical Verification for Wildfire Aware Power Shutoff

#30
by clu360 - opened

Caleb Lu and Xiao Liu · H. Milton Stewart School of Industrial and Systems Engineering, Georgia Institute of Technology
Primary Email of Contact: clu360@gatech.edu

Repository and reproducible demos · GENCO and GridSFM checkpoints · Three-page technical submission

Why OPS is a useful testbed for grid foundation models

Wildfire-aware Optimal Power Shutoff (OPS) aims to reduce exposure from energized transmission lines while retaining electricity service. Following Rhodes, Ntaimo, and Roald (2021), we investigate a predict-then-optimize workflow that proposes line de-energizations, adjusts selected load-service controls, evaluates the resulting operating states, and finally checks selected decisions using nonlinear AC physics. This is a combinatorial task: changing one line can redistribute flow throughout the network.

Our central question is not only whether a model predicts a grid state accurately, but whether its predictions lead to better AC-verified operational decisions. We first established the workflow on GOC-500 using GridSFM, then transferred it to a modified Texas2k system using GENCO-OPF, real weather-derived exposure, and grid-to-task fine-tuning.

Before using a learned evaluator, the original OPS formulation from Rhodes et al. weighs served demand against wildfire exposure while enforcing component and power-flow constraints. Our computationally bounded version expresses the same central preference as

Minimize  J = λR × normalized wildfire exposure + (1 − λR) × load shedding
Decisions: line status z; requested load service α; generation response under the evaluator's control contract

The original OPS co-optimizes network decisions and operational recourse using a DC formulation. Our application differs: we first propose topologies, then use a learned electrical-state evaluator with a bounded load-service search, and finally run nonlinear AC audits. This is a screen-and-verify heuristic, not a claim of replacing the exact constrained OPS formulation.

Original OPS formulation versus our surrogate-assisted screening

Surrogate-assisted OPS and AC-verification workflow

The current evaluator screens candidate topologies with at most two planned shutoffs, followed by a bounded five-load-control search with up to 20 model objective calls per topology. Exact AC Reference A fixes topology and requested service, then optimizes economic dispatch. Reference B1/B2 asks how much service that topology can physically deliver, followed by an economic tie-break. These are audits of selected solutions, not global optimality certificates or risk-constrained corrective OPF.

1. GOC-500: a controlled laboratory for adaptation and downstream decisions

We began with three constructed diagnostic hazard patterns: a high-risk line with low service consequences, one with high service consequences, and one with an alternate network path. These interpretable cases allowed us to establish the topology-proposal → GridSFM state evaluation → recourse → AC-reference workflow before introducing geographic hazard data.

We compared the released GridSFM checkpoint M0 with M1 (1,000 intact-grid cases), M2 (M1 plus 500 intact cases), and M3 (M1 plus 500 N−1 cases). Across a common 375 intact + 375 N−1 held-out test, M2 had the lowest intact loss and M3 the lowest N−1 loss. Intact active branch-flow MAE fell from 0.0745 p.u. (M0) to 0.0350 p.u. (M2).

Fine-tuning convergence is recorded across ten epochs of additional intact-versus-N−1 adaptation. The two continuation paths trade off intact and contingency accuracy; this is not uniform improvement in every physical metric.

GOC-500 N−1 validation loss during sequential adaptation

GOC-500 convergence on a common N−1 validation split: ten-epoch continuation from M1 with either 500 additional intact cases (M2) or 500 N−1 cases (M3). This is training/validation convergence, not OPS-search convergence. Source traces.

GOC-500 fine-tuning agreement and measured screening speed

A concrete OPS result under designed hazard: J-S1

The J-S1 diagnostic assigns elevated exposure to a target line whose removal has relatively low expected service consequence. On the surrogate-evaluated J-S1 risk–service frontier, the released GridSFM has normalized risk near 0.47 with zero shedding, while intact-adapted M2 reaches roughly 0.42 with negligible shedding. This illustrates the opportunity for selected K≤2 de-energizations to reduce the predicted exposure in controlled scenarios. It is not a certified exact-AC reduction, nor does the gap isolate topology choice from model calibration and load-service recourse.

J-S1 exact empirical GridSFM risk–service comparison

J-S1 empirical GridSFM-evaluated Pareto frontier from the original research figure, traced from the supplied source PDF. The plot records native predictions, not certified exact AC reductions. Retained GOC Pareto evidence.

The strongest lesson came from comparing model predictions with exact AC-recovered decisions. For M2 versus M0, mean state NRMSE fell 42% and absolute risk discrepancy fell 76%, yet mean AC-audited OPS objective improved by only about 1.1%; M1 attained the best mean audited objective. Thus, substantial prediction gains did not translate proportionally into decision gains. The completed GOC study also includes empirical risk–service frontiers, fixed-decision reference comparisons, and a 525-solve warm-start study.

Computational evidence: on 54 matched fixed decisions, released GridSFM achieved a 3.59× paired-median complete state-evaluation speedup versus AC-OPF/IPOPT on the tested CPU environment (95% bootstrap interval 3.48–3.68). A separate warm-start comparison showed only modest solver-time benefits. These are specific evaluation boundaries, not whole-OPS or GENCO/Texas2k acceleration figures.

2. Texas2k: geographic wildfire exposure reveals a harder problem

We then moved to modified Texas2k (2,751 buses, 5,344 branches), using operating Scenario 16 and the weather-derived June 23, 2023, 4:00 PM CDT wildfire-exposure snapshot. Unlike the designed GOC diagnostics, the geographic exposure is not constructed to guarantee an obvious or favorable shutoff decision. Our loading-dependent risk is an exposure proxy, not a calibrated ignition probability, and the synthetic electrical network is not a utility operating study.

The Stage K comparison screened candidate states with GridSFM, DC, and exact AC. Its smoke-benchmark-based extrapolation estimated 4.34 hours of serial GridSFM screening on V100 versus 51.47 hours for AC on CPU, approximately 11.9× for the tested configuration. This is a projected hardware-dependent screening comparison, not a measured GENCO speedup or full end-to-end OPS advantage.

The contrast with J-S1 is central: in our GOC diagnostic, high-risk line selection offered clear surrogate-evaluated risk reductions at very limited shedding. In the geographic Texas2k snapshot, taking out two lines by itself is not enough to ensure a risk reduction under exact AC conditions. Meaningful decreases in the historical DC/AC comparisons are accompanied by much more aggressive continuous load-service and dispatch recourse.

More importantly, the continuous operating decision often dominates the result in this scenario. At λR = 0.8, historical DC and AC selected operating points achieved audited normalized risks 0.488 and 0.474, but with 43.76% and 34.61% load shedding respectively. Their Reference B recovery can restore essentially full service, although the risk increases to 1.100 and 1.084. Consequently, opening attractive lines is not sufficient: how generation and service are reoptimized under exact physics matters greatly. These historical methods have broader dispatch and service recourse than our GENCO-OPF wrapper, so this is not a hardware- or control-matched ranking.

Texas2k incumbent surrogate-search convergence

Texas2k topology-search convergence is a record of the best native OPS merit found as candidates are evaluated; it is not convergence to a certified global or AC-feasible optimum.

For comparable additional context, see the Texas Stage K/L/M exact reference comparison and empirical native risk–service frontiers. Native DC, AC, GridSFM, and GENCO methods do not share identical control freedom or prediction physics; exact references are the more meaningful outcome comparison.

3. GENCO-OPF: fine-tune to the grid, then to the operational topology distribution

With the same 500-example total training budget, we evaluated three GENCO-OPF adaptations:

Final checkpoint Adaptation data What it tests
G500 500 intact-grid cases Target-grid adaptation
G100 → R400 100 intact + 400 random N−1/N−2 cases Generic contingency exposure
G100 → W400 100 intact + 400 wildfire-ranked N−1/N−2 cases Task-relevant outage exposure

The wildfire-ranked cases are not AC-OPS-optimal labels. Each final checkpoint screened 301 topologies and 6,020 surrogate objective calls, sharing the initial 50 single-line candidates while generating model-specific double-outage candidates from the five top-ranked parents. We evaluated held-out G/R/W validation strata and exact AC references for each selected finalist.

GENCO physical validation and selected-decision audit

The validation results show mixed transfer. On the intact G stratum, average active-power imbalance remains roughly 51–52 MW per bus, while sequential adaptation lowers average reactive imbalance from 20.6 to about 16.6–16.7 MVAr. However, mean worst-bus active imbalance increases from 6,265 MW (G500) to 9,312/9,841 MW (R/W). Such neural states cannot be called AC feasible.

The selected decisions reveal an even more instructive inversion:

Checkpoint Selected outage pair Native OPS objective J ↓ Audited Reference A J ↓ Audited risk ↓
G500 117;1548 1.0166 0.9319 1.1641
G→R 117;281 1.1601 0.8713 1.0890
G→W 117;281 1.2091 0.8714 1.0891

G500 looks best under its native score; contingency-adapted checkpoints look better after AC economic recovery. Both R and W choose the same outage pair and give almost identical audited results. All three audited risks remain above the stored intact-risk baseline of 1, so this is not a demonstrated operational wildfire-risk reduction. Because the K2 search pools differ and the AC references replace predicted dispatch, this inversion is not a common-candidate ranking test or a causal estimate of the benefit of specific training examples.

The difference from GOC-500 is revealing. In constructed diagnostics, selected topology changes can produce clear exposure reductions; on this Texas snapshot, continuous recourse and AC recovery largely determine the risk–service outcome. The model's prediction accuracy, operating control interface, candidate search coverage, and exact AC feasibility all become critical.

4. What this opens up

Near term: Because the Texas experiments reveal the limits of extensive continuous surrogate optimization at each topology, we propose separating broad discrete screening from accurate physical recourse: screen a much larger set of candidate topology decisions cheaply, use GENCO to shortlist promising choices, then solve risk-aware AC recourse only for the finalists and rerank using exact outcomes. This is a proposed extension, not the method that generated the reported results. Evaluate decision recall, ranking disagreement, AC objective gaps, service recovery, and whole-workflow runtime against DC/AC benchmarks at matched control budgets.

Adaptation study: expand grid-only and task-only learning curves, test how many intact versus contingency samples to allocate, and examine transfer as planned shutoff budgets move beyond K≤2 to K=5, 10, or 20. These are prospective investigations, not security guarantees.

Broader view: grid foundation models can become reusable components of scientific decision workflows: simulate → generate evidence → adapt → screen → physically verify. This study illustrates the need for that verification layer rather than claiming deployment-ready autonomy.

Reproduce and build on the work

Repository · Documentation and reproduction guide · Public model archives · GOC-500 technical supplement

The release includes model selectors, certified weights, GOC-500/Texas result tables, and four notebooks. It provides a real public IEEE-14 GENCO interface example with genco-ops public-genco --output outputs/public_genco --execute, and regenerates figures from retained compact evidence without PACE. Exact modified Texas electrical inputs remain private, so this is not a public full Texas2k rerun. GridSFM is the GOC-500 precursor; GENCO-OPF is the Texas2k challenge experiment. Native fine-tuned GridSFM Texas OPS/AC was pending in the published evidence cut.

References: Rhodes, Ntaimo & Roald, 2021 · GENCO (Puech et al., 2026) · GridSFM.